Is there a way to review the Digital Input/Digital Output LED light history of a Siemens S7-1200 PLC?
If so, is it through the web portal or through Simatic and can someone point me in the direction of where to find such information?
Thanks - will save me a site visit if possible in any way.
Upvotes: 2
Views: 1048
Reputation: 242
There is no built in DI/DQ history for the S7-1200.
However, if you have some form of TCP/IP connection, this can be done quite easily.
When you call outputs in your main program, use a tag based calling system. Reference that tag, and have the tag's output be:
For inputs, just send a message on the rise and fall of each input
It is likely easiest to hold this DI/DQ history on the server that is hosting this TCP/IP connection rather than the PLC itself.