We're evaluating cpppo to talk to various Rockwell Automation PLCs. We have address ranges in form "N25:00" (N = integer, file number 25, file offset 0), but EtherNet/IP seems to want @<class>/<instance>/<attribute>
.
How do you translate from one to the other?
If tags were defined in these PLCs, is there a way to get a list of them, or information about them? We have no ability to change the PLCs, and usually can't see the ladder logic/configuration in them.
cpppo's list_identity, list_interfaces, and list_services all work, but don't return anything that seems to translate:
List Services 0 from ('10.91.xxx.yyy', 44818): {
"count": 1,
"item[0].communications_service.capability": 32,
"item[0].communications_service.service_name": "Communications",
"item[0].communications_service.version": 1,
"item[0].length": 20,
"item[0].type_id": 256
}
List Interfaces 0 from ('10.91.xxx.yyy', 44818): {
"count": 0
}
Upvotes: 2
Views: 532
Reputation: 96
You left out an important detail info. What kind of Rockwell PLC? The N25:00 address could be the older PLC type like SLC5, PLC5 series. On the other hand Ethernet/IP is used in the newer tag-based PLC like Compactlogix, ControlLogix PLC.
btw, there's PyLogix that will talk to the newer type PLC.
Upvotes: 2
Reputation: 163
It looks like you will need a gateway of some type. I'm using a commercial product called cogent data hub to get my rockwell data into a SQL database. Not sure that helps you much.
At the very least you'll want some sort of DDE/OPC server. You can use RSLinx Classic for that if you bought it.