I'm having problems with my PLC s7-1200 CPU 1211C, after I connected to 24VDC LED status only turn on Run/Stop LED, but in orange colour, not Green, my PLC is new and I don't how to fix It.
Note: I'm using TIA Portal V14 and also It doesn't recognized my PLC.
Upvotes: 2
Views: 8893
Reputation: 2442
To setup your PLC in TIA-portal and follow the steps below:
ip address
and device name
in the PROFINET interface [X1]
in the device view
properties;accessible devices
next to the Go offline
button and search the the plc it should find it; show
;online access
of the device; online & diagnostics
;ip address
and device name
of the online device.Now you should be able to download. The orange Rx/Tx LED will start blinking. When finished the Error LED is turned of and Run/Stop LED becomes green. Voila... your done.