I am working on a project with a master computer connected via a CANOpen network to 4 slaves.
At each time step, the computer receives a measurement message from each slave, and sends them a control message. In total, 4 messages are received and 4 messages are sent at each time sample.
The message sent is a PDO with 6 data bytes (8 bytes including COB-ID) The message received is a PDO with 8 data bytes (10 bytes including COB-ID)
My CAN network is configured at 1Mbit/s, and I run my program at 1000 Hz (1 ms sampling time). As the total load resulting from the messages described is 576 bits/cycle, the total load expected in the network is 576kbit/s, or 57%.
What I see, however, is that:
What I'd like to know is whether my way of calculating the CANOpen network load is correct. For instance, are there any protocol-specific handshakes, CRCs, or any sort of extra bytes sent to make the network simply work? It's nothing I could see in the wiki page of CANOpen, but I do know there are such appendices to messages in the original CAN bus standard.
Upvotes: 0
Views: 440
Reputation: 3839
In a CAN message, there is more than the data to be transmitted. There is also the arbitration ID (11- or 29bits, depending on whether you use CAN 2.0A or 2.0B), there is a 15 bit CRC, an 7 bit EOF marker, the control field and also some other reserved bits. Depending on the data, there may also be stuff bits.
Using CAN2.0B and assuming 48 bits (6 bytes) of data, you will get a message size of roughly 132 bits and roughly 151 bits for your 64 bits messages.
Summing this up, you will get roughly 1132 bits per cycle which is too much for a 1Mbit/s bus and 1000 Hz.
Hope that helps.