Unable to scan Beckhoff KL 2502 module

I was trying to scan Beckhoff KL 2502 (PWM op module) in my beckhoff system through by PC, but this module is not visible when I scan the devices. I added the respective xml file to the twincat folder and still it is not visible in the scan. I tried to add the module manually in the devices it is throwing up error. Has anyone faced the same issue before?.

Any possible solutions are welcome.

Thanks a lot.

#Twincat3 #Twincat #PLC #Beckhoff #hmi #SPS

Upvotes: 0

Views: 539

Answers (1)

Jacek Domański
Jacek Domański

Reputation: 640

What module is before KL2502? If it is an EL module, you need BK1250 module to connect Bus terminals and EtherCAT terminals.

One BK1250 is enough, but the order is important. First, the PLC, then EL modules, coupler and KL modules. Something like this should work fine:

CX9020 > EL9189 > EL9188 > EL1809 > EL2809 > BK1250 > KL2502.

If any more EL modules were to be added, they should be placed between EL2809 and BK1250. If any more KL modules were to be added, they should be placed after KL2502