I was trying to scan Beckhoff KL 2502 (PWM op module) in my beckhoff system through by PC, but this module is not visible when I scan the devices. I added the respective xml file to the twincat folder and still it is not visible in the scan. I tried to add the module manually in the devices it is throwing up error. Has anyone faced the same issue before?.
Any possible solutions are welcome.
Thanks a lot.
#Twincat3 #Twincat #PLC #Beckhoff #hmi #SPS
Upvotes: 0
Views: 539
Reputation: 640
What module is before KL2502
? If it is an EL
module, you need BK1250 module to connect Bus terminals and EtherCAT terminals.
One BK1250
is enough, but the order is important.
First, the PLC, then EL
modules, coupler and KL
modules. Something like this should work fine:
CX9020 > EL9189 > EL9188 > EL1809 > EL2809 > BK1250 > KL2502
.
If any more EL
modules were to be added, they should be placed between EL2809
and BK1250
. If any more KL
modules were to be added, they should be placed after KL2502